电气导管壁厚规范要求,电气导管管材选择参考

来源:电工天下时间:2016-08-26 05:50:18 作者:老电工手机版>>

电气导管壁厚规范要求

管材型号外径(mm)内径(mm)壁厚(mm)理论重量(kg/m)长度(m)
标准值调整度最小值最大值最小值最大值标准值调整度最小值最大值
焊接钢管DN1521.3±0.420.921.714.616.82.8±12.5%2.453.151.286
DN2026.926.527.320.222.41.66
DN2533.733.334.126.128.53.22.83.62.41
DN3242.442.042.834.837.23.36
DN4048.347.948.740.0242.583.53.063.943.87
DN5060.3±0.559.860.851.9254.685.29
DN65(70)76.175.676.667.0469.943.83.334.287.11
DN80(75)88.988.489.479.482.44.03.54.58.38
DN100114.3113.8114.8104.8107.810.88
DN125139.7139.2140.2130.2133.213.39 【电气导管壁厚规范要求】
DN150168.3167.8168.8157.68160.924.53.945.0618.18
根据《低压流体输送用焊接钢管》(CB/T3091-2001)
镀锌钢管与焊接钢管相同,重量按表加3%-6%。
衬塑钢管DN1521.3±0.420.921.712.813.42.8±12.5%
+(1.5±0.2)2.45+(1.3-1.7)3.15+(1.3-1.7)6
DN2026.926.527.318.318.9
DN2533.733.334.124.024.83.22.8+(1.3-1.7)3.6+(1.3-1.7)
DN3242.442.042.832.833.6
DN4048.347.948.738.039.03.53.06+(1.3-1.7)3.94+(1.3-1.7)
DN5060.3±0.559.860.850.051.0
DN65(70)76.175.676.665.066.23.83.33+(1.3-1.7)4.28+(1.3-1.7)
DN80(75)88.988.489.476.577.94.0±12.5%
+(2.0±0.2)3.5+(1.8-2.2)4.5+(1.8-2.2)
DN100114.3113.8114.8102.0103.4
DN125139.7139.2140.2128.0130.0
DN150168.3167.8168.8151.0153.04.5±12.5%
+(2.5±0.2)3.94+(2.3-2.7)5.06+(2.3-2.7)
根据《给水衬塑复合钢管行业标准》(CJ/T136-2001)
管材型号外径(mm)内径(mm)壁厚(mm)理论重量(kg/m)长度(m)
标准值调整度最小值最大值最小值最大值标准值调整度最小值最大值
PVC电工套管(中型)Φ1616-0.315.71614.616.81.5-0.31.21.51.284
Φ202019.72020.222.41.551.251.551.66
Φ252524.72526.128.51.81.51.82.41
Φ323231.73234.837.22.11.82.13.36
Φ404039.74040.0242.582.32.02.33.87
根据国际电工委员会制定的IEC614-1:1994和IEC614-2:1994《电气装置用导管规范》
UPVC塑料排水管De4040+0.34040.335.236.32.0+0.42.02.44(可按层高定制)
De50505050.345.246.3
De75757575.369.670.72.32.32.7
De110110+0.4110110.4102.41043.2+0.63.23.8
De125125125125.4117.4119
De160160+0.5160160.5150.8152.44.04.04.6
De2002005.0
柔性铸铁管DN5061(58)+2.0
-1.04.3(3.5)-0.5一般为1.5米及3米(可定制)
DN7586(83)4.4(3.5)
DN100111(110)4.8(3.5)
DN125137(135)+2.0
-2.04.8(4.0)
DN150162(160)4.8(4.0)
DN200214(210)5.8(5.0)-1.0
DN250268(274)+2.0
-2.56.4(5.5)
DN300318(326)7.0(6.0)
根据《排水用柔性接口铸铁管及管件》(GB/T12772-1999)注:()内为厂家提供数据
铝塑复合管162020+0.32020.315.416.51.90+0.41.902.30盘管(一般百米一盘)
2025252525.319.520.82.25+0.52.252.75
2632323232.325.226.52.902.903.40 (电工天下 www.dgjs123.com)
324040+0.44040.430.832.44.00+0.64.004.60
415050+0.55050.539.641.54.50+0.74.505.20
管材型号外径(mm)内径(mm)壁厚(mm)理论重量(kg/m)长度(m)
标准值调整度最小值最大值最小值最大值标准值调整度最小值最大值
铝塑复合管516363+0.66363.649.451.66.00+0.86.006.80
607575+0.77575.75860.77.50+1.07.508.50
根据《建筑给水铝塑复合管管道工程技术规程》(CECS105:2000)
KBG管Φ1616-0.315.71613.5414.161.0±0.080.921.08
Φ202019.72017.5418.16
Φ2525-0.424.62522.022.81.2±0.11.11.3
Φ323231.63229.029.8
Φ404039.6403737.8
PP-R管De20S5
PN1.0+0.32.02.3S4
PN1.25+0.42.32.7S3.2
PN1.6+0.42.83.2
De25+0.42.32.72.83.2+0.53.54.0
De322.93.3+0.53.64.1+0.64.45.0
De40+0.53.74.2+0.64.55.1+0.75.56.2
De50+0.64.65.2+0.75.66.3+0.86.97.7
De63+0.75.86.5+0.97.18.0+1.08.69.6
De75+0.86.87.6+1.08.49.4+1.210.311.5
De90+1.08.29.2+1.210.111.3+1.412.313.7
De110+1.110.011.1+1.412.313.7+1.715.116.8
De125+1.311.412.7+1.514.015.5+1.917.119.0
De160+1.614.616.2+1.917.919.8+2.321.924.1
根据《建筑给水用无规共聚聚丙烯(PP-R)管道工程技术规程》(DBJ13-50-2003),以上数据均为壁厚。
给水交联聚乙烯管(PEX管)De20201.9卷长100米
De25252.3
De32322.96米
De40403.7
De50504.6
相关文章
  • 电气设备绝缘老化的影响因素

    电气设备绝缘老化的影响因素

    电气设备的绝缘老化的影响因素,绝缘材料的寿命与老化时间的关系,包括热老化、电老化、机械力老化、湿度老化、化学老化等,绝缘老化最终导致绝缘失效,电力设备不能继续运行。

    时间:2022-09-18 07:44:49

  • 电气设备如何保证倒闸操作准确率?

    电气设备如何保证倒闸操作准确率?

    电气设备保证倒闸操作准确率的常用方法,倒闸操作规范准确与否关系到人身和设备的安全,将电气设备由一种运行状态转变到另一种运行状态,就需要一系列的倒闸操作,强化倒闸操作理论学习,加强实际操作演练。

    时间:2022-09-15 08:03:29

  • 电气设备常用文字符号参考图解

    电气设备常用文字符号参考图解

    有关电气设备常用文字符号参考,包括基本文字符号,辅助文字符号,电气设备常用图形符号大全,电气设备常用文字符号的中文说明详解。

    时间:2022-09-15 06:41:40

  • 电气设备与电气照明节能措施详解

    电气设备与电气照明节能措施详解

    电气设备与电气照明节能措施,包括工厂电气节能措施,供配电设备节能措施,电气设备节能措施,电动机的节能措施,无功功率补偿装置的应用,节能技术改造的实施,以及企业照明系统的更新等。

    时间:2022-09-15 05:54:58

  • 爆炸危险场所防爆电气设备的选型注意事项

    爆炸危险场所防爆电气设备的选型注意事项

    有关爆炸危险场所防爆电气设备的选型注意事项,选择使用于爆炸危险场所的电气设备前,明确燃炸危险场所环境的类别,环境中爆炸性气体混合物的爆炸级别,周围环境对防爆电气设备的选型要求。

    时间:2022-09-14 18:50:58

  • 电气设备倒闸操作票制度及倒闸操作术语

    电气设备倒闸操作票制度及倒闸操作术语

    有关电气设备倒闸操作票制度及倒闸操作术语,在全部停电或部分停电的电气设备上工作,必须执行操作票制度,包括操作票上的内容,填写操作票的要求,操作票填写检查项目内容等。

    时间:2022-09-14 18:50:23

  • 电气设备外壳不同防护等级标志说明

    电气设备外壳不同防护等级标志说明

    电气设备外壳不同防护等级标志说明,电机和低压电器的外壳防护包括两种防护,外壳防护等级标志,第一位数字表示第一种防护型式等级,第二位数字表示第二种防护型式等级。